Damper
Comments
-
The damper never opened? If so, stop.. shutdown the boiler. Get it fixed.0
-
Can I do this?0
-
When you say the "Damper never went on" do you mean it never opened? If that's the case, that will let carbon monoxide enter your home. You need to get a service tech out to check that before you run that boiler again. The safety features on the boiler controls should have shut the burner down when the damper failer to open. Are you sure it never opened? Is the shaft that runs through the damper turning causing the boiler controls to think the damper is open? If that's the case, check to see how that damper is mounted on that shaft. Is it spot welded or clamp and screws? If clamped, did the screws simply come loose?0
-
Before I used to hear the damper rotate now I don't hear it0
-
-
looks closed.
don't use it.
get it repaired or replaced.0 -
Has to be fixed!0
-
Any one know of someone in Nassau Long Island?0
-
How can you tell if it's opened or closed i those pictures?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
With a flashlight and a mirror you could look up and tell.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
That was my first though, but I assumed others could tell by the pictures shown.BobC said:With a flashlight and a mirror you could look up and tell.
Bob
I didn't think the damper would allow the burner to ever fire unless it opened. If it's stuck shut isn't there a way to manually open it and lock it open?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
It's close! and when I turn the thermostat up the boiler won't fire. how long do this things last?0
-
I've heard they fail from time to time. Hopefully someone will say how to manually open it.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
-
I manually open it but now the boiler won't Fire!0
-
Did you just flip the switch on it, or did you physically manually open it?
The burner shouldn't fire unless it's actually open and if it burned out flipping the switch won't work.
Of course there is always the chance the damper has nothing to do with it and something else failed.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I manually open it0
-
If the vent damper didn't open I would think it would cause the blocked vent switch to trip open. That is manual reset. If this is beyond what your comfortable with find a pro.0
-
That boiler looks like it might be a Burnham. According to manual the vent damper needs to open to operate the boiler. if one is not used there is a jumper that is installed in the vent damper wiring harness. Therefore I find it hard to believe the boiler fired up with the damper not operating properly and if it did why didn't the blocked vent switch trip open and turn off the boiler? Get a pro in to figure this out.0
-
Vent dampers fail quite often..Yes you can jump it out…for trouble shooting purposes….Many times it the 4 prong connector at the dampener has issues…The pins or sockets become loose, making for a bad connection….Wiggle the connection….Even easier get a meter and measure voltage..Please do not just lock it open and run it…You could up in a not so good situation….I am sure the manufacture,of the failed units are on a nice sales vacation, while home owners and service people fix there crap...0
-
@ChrisJ zoom in on the first pic. Look at the damper bar. The flat indicates the direction the damper is in. It's closed.ChrisJ said:How can you tell if it's opened or closed i those pictures?
I have to shake my head when homeowners want to jumper a safety device. Guess they haven't heard of CO poisoning deaths in the news.0 -
Abracadabra said:
@ChrisJ zoom in on the first pic. Look at the damper bar. The flat indicates the direction the damper is in. It's closed.ChrisJ said:How can you tell if it's opened or closed i those pictures?
I have to shake my head when homeowners want to jumper a safety device. Guess they haven't heard of CO poisoning deaths in the news.
I don't consider having the damper manually open as "bypassing a safety device" The damper is an energy saver and as long as it's disconnected in the open position what is the problem?
Further more, if something did go wrong the spill switch is also there to protect the user. Obviously we don't want to rely on a "worst cast scenario last resort safety device" like the spill switch but it is there.
My view on the entire thing right now is we are trying to get the person's heat back on and that he would replace the damper.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Yea, on that damper, the flat bar is an indicator of the damper position. On a damper where carbon monoxide is an issue, I wouldn't depend on the spill switch. He should be able to find a replacement damper locally. If not, I'd take the damper out completely by taking that flat bar and damper out, plug the holes temporarily, then he can jumper it as there will be no risk of holding gases in the house.0
-
I switch the manual button to open the damper but the boiler still not firing. I looked under the the hood and check and saw the damper open. Does this mean is not the damper? That is causing the boiler not to fire. Is there something else I should check?0
-
Do you have the manual for the vent damper? There is a trouble shooting guide in the manual. If your not comfortable following the guide call a pro to get your heat fixed. If the vent damper motor assembly is bad the boiler will not fire even when jumped out.0
-
I'd start by checking the sensor/damper control on the boiler. It is quite possible that has failed. Make sure all the connections are good. If they are, you are going to have to do (or have a tech) more dianostics but the fact that the boiler won't kick on coupled with the fact the damper didn't open automaticcally probably means you have identified the source of the problem and that the safety devices did their job.0
-
Chris, I agree with you. But it sounded like the boiler was operating and he didn't hear the damper move. His pictures show the damper closed. I'm assuming it is somehow bypassed, otherwise the burner should not light.ChrisJ said:
I don't consider having the damper manually open as "bypassing a safety device" The damper is an energy saver and as long as it's disconnected in the open position what is the problem?
0 -
On my WM the vent damper was originally after the LWCO so if the LWCO failed, or a low water condition existed the vent damper would remain closed and of course the burner wouldn't fire.
Ah.Abracadabra said:
Chris, I agree with you. But it sounded like the boiler was operating and he didn't hear the damper move. His pictures show the damper closed. I'm assuming it is somehow bypassed, otherwise the burner should not light.ChrisJ said:
I don't consider having the damper manually open as "bypassing a safety device" The damper is an energy saver and as long as it's disconnected in the open position what is the problem?
Not sure what went down. It sounds like somehow the boiler did operate with it shut, but now won't. The only way I can see that is if the switch in the damper failed, allowing the burner to get power even though it was closed and that tripped the spill switch.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
make sure damper is open by rotating it.
set it to manual
follow black and white wire on side of boiler heading to the draft hood on the back they go to a thermal spill switch that can be reset by pushing the red pin between both wire connectors on the switch.
make sure you have a good draft..if not shut down boiler and get the chimney checked1 -
if you cycle the power while the damper was open it stays open as long as the t-stat is calling for heat.you have to turn the t-stat off to have the damper close then try it again0
-
So I had a plumber come out and test the damper. He reset the thermal spill switch and checked all connections from the t-stat to damper. Which I had already done with no success. he removed the pressuretrol and "pigtail" and cleaned it. Then, said "the pressuretrol was not allowing the boiler to turn on." Why didn't I think of that? That cost me $185.00. Overpriced? it was after hours. He left around 9:30pm. Nonetheless, thank you all for your help and comments. Im so glad to have heat now.0
-
Well,
We should not be discussing pricing on here however,
I don't know, personally I think knowing it's working correctly is worth a measly $185. What do you think?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Plugged pigtail. Some pressure got caught between the pressuretrol and the clog, holding the pressuretrol "off". Definitely not the first time I've seen this happen.
And, we don't discuss pricing on this site.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Cant agree more about pricing….If they talk price lock them out….Yup pigtails clog often…Thats why boiler owners need to have the boilers serviced...0
-
Sounds like money well spent to me. Came out to the customers house on a Saturday night and restored their heat is a safe manner. Price is not to be discussed here, but before you question the price charged don't forget all contractors have overhead that needs to be paid. Their trucks, insurance, advertising, supplies, tools, employees, the shop, the accountant, heat for the shop, the list goes on and on.0
-
True! but when I asked him what's in a yearly maintanence he said clean the burners check safety devices and add cleaning additive to boiler. When I asked him abt skimming he kind of shook his head and said no need for that just additive will work. What should be done on a maintenance visit?0
-
My apologies abt discussing price!0
-
Never use a cleaning additive.Steaming101 said:True! but when I asked him what's in a yearly maintanence he said clean the burners check safety devices and add cleaning additive to boiler. When I asked him abt skimming he kind of shook his head and said no need for that just additive will work. What should be done on a maintenance visit?
I run water treatment, but clean the old fashion way.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
My name is Danny Scully and I operate Scully's Plumbing in the Nassau County area of Long Island. We would be glad to offer you a more detailed maintenance program, which could include skimming/wand cleaning your boiler.0
-
Skimming only has to be done after significant piping work or boiler replacement. Companies want to use additives because the cost of having someone babysit a boiler for what could be several 2-3 hour skimming sessions is just too high. They should show the homeowner how it's done and tell them it may take several sessions to get rid of all the oils.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
For the record, the pic Chris posted was a gas explosion in Oldham, England, where an abusive drunk cut the gas pipe in his house and blew it up to retaliate against his girlfriend. Fortunately they threw him in jail where he belongs. But these kinds of things happen through negligence and incompetence as well.
If you think about it, a plugged pigtail can permit a boiler to reach highly dangerous pressures, if there is no pressure trapped between the clog and the control. The boiler pressure would not be able to reach the control thru the clog. Now, at least your pressure control can work properly and safely.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements