terms in a hot water heating system and help needed on wiring
heatingFun
Member Posts: 84
I am trying to figure out how to use the Taco SR504-exp-4 Switching Relay with my Alpine 105 gas boiler due to the changing from one zone to 3 zones. I am not very clear some terms on the instructions. Please help me. My system doesn't have a hot water sub-system attached. It is a winter water heating only system.
System pump ---- the pump for individual heating zone.
DHW pump ---- the pump for the hot water sub-system(for shower, kitchen, not for the winter water heating system)
Boilder pump ---- the pump close to the boiler and help the water circulating to the boiler
Primary pump ---- the boiler pump?
Priority ---- for DHW only?
For the wiring, I have modified a sample wiring diagram coming with the Burnham Alpine 105 boiler installation manual. Please help me wire it right. The one with red lines is my wiring plan.
System pump ---- the pump for individual heating zone.
DHW pump ---- the pump for the hot water sub-system(for shower, kitchen, not for the winter water heating system)
Boilder pump ---- the pump close to the boiler and help the water circulating to the boiler
Primary pump ---- the boiler pump?
Priority ---- for DHW only?
For the wiring, I have modified a sample wiring diagram coming with the Burnham Alpine 105 boiler installation manual. Please help me wire it right. The one with red lines is my wiring plan.
0
Comments
-
Will your system utilize outdoor reset and what temp do you intend to store DHW in the tank and what sensor are you using ?You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
there is a outdoor sensor installed. there is no DHW tank attached to the system. we use a separated electrical hot water tank for shower.0
-
Your drawing will work . Make sure to jumper the priority zone if your are not using it . Let the boiler turn the boiler pump on and off and the Sr will do the rest .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
Do I still need to connect the system circulator output from boiler to the ZC on the SR504-exp-4 switching relay, like the one on the sample wiring diagram? I updated the diagram with blue lines. It is better now?
0 -
Could you draw how the near boiler piping will be done ? The boiler circulator should be on whenever the boiler is on , Your system circulators are the 3 pumps wired to the SR control . That should be all you need if in fact there are 4 pumps total connected to this system . No need for any blue lines whatsoever unless I am missing something .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
-
There ya go . No blue lines , just let the boiler turn on the boiler circ and let the SR control do the rest .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
I agree with Rich. Unless your boiler is heating your potable hot water also, the blue lines drawn are not needed.0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements