ek system 2000

Paul_69
Member Posts: 251
in Oil Heating
When does puff switch cut out on system 2000? Are they adjustuble and on lower chimney draft are they going to be a constant problem? Thx
0
Comments
-
The puff switch will open at anywhere between +.06 to +,10" depending on how old it is. The newest ones are set to open at approx. +.10" wc. They are not meant to be adjusted in the field. Check your draft over fire during a run cycle. If it's positive, you have a draft issue. It it's negative, or a very low positive, and the switch still opens then replace it.0
-
Also you want to make sure the proven tube, tee, and nipple are clean and free flowing. How old is the EK? Possible older model with the baffle?0
-
Bill, just a general question about the switches. Thx0
-
No problem Paul. Wasn't sure if you were having some issues.0