Water exiting thru radiator vent
Steaming101
Member Posts: 30
I'm getting abt 2-3 cups of water exiting thru my radiator vent. Has anyone had this happen? It happens at the beginning of each heating cycle.
0
Comments
-
Check that the rad valve is completely open allowing the water to drain. Also check the pitch of the rad with a level. Should have a slight pitch toward the rad valve.0
-
Send pictures of your boiler header
What floor is this radiator on?
What operating pressure are you running?Since 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER
A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-05930 -
Also check your main vents, and pressure. If you have inadequate main vents, then more wet steam will be pushed up into the radiator. The radiator vents should be virtually silent, and dry. If they are noisy, then that is a sure sign of lack of main venting.
If the boiler has been recently replaced, then the water may be dirty, and need skimming, or the supply piping may be improper.--NBC0 -
I check for pitch which the radiator has, the valve is completely open. I have 2 Gordon #1 vent in the mains which are big enough I would think.0
-
The radiator is on the 1st floor and the pressure Main is 2 and diff is set 1 1/2. But it seems like the water is kind of dirty? https://us.v-cdn.net/5021738/uploads/editor/m7/z7wg11c1t39s.jpg
https://us.v-cdn.net/5021738/uploads/editor/12/d849kb0u9cl3.jpg
https://us.v-cdn.net/5021738/uploads/editor/t8/ps7ykdjlf2i7.jpg
https://us.v-cdn.net/5021738/uploads/editor/x2/bdar3ketvb9q.jpg
https://us.v-cdn.net/5021738/uploads/editor/3n/9ethk6jwq7fz.jpg
https://us.v-cdn.net/5021738/uploads/editor/r1/0a0h8u4j2x5o.jpg0 -
Is it just the one radiator? Even though you say the valve is open all the way, are you sure that it is, in fact open? Sometimes those old valves will come apart internally and be partially closed. you will have to take the radiator loose and look at the inside of the valve or take the bonnet off of the top of the valve and look at it. Also two other things to look at. What is the boiler pressure? You need to make sure your pressuretrol is working properly. They can fail and they certainly get out of adjustment (way out). Too much pressure will push water out of the boiler and into the mains and subsequently into the radiator runs. The other thing to check is that radiator run off of the main. Is it also pitched back towards the main soo that water can run out of it? Finally, I know from your earlier posting that you haven't had that boiler skimmed in a long time, if ever. That needs to be done.1
-
Not sure what boiler that is, but your near boiler piping leaves something to be desired. Whoever installed that should have used both risers out of the boiler into a header. The way it is now, your boiler is pushing wet steam into the mains, especially with the cutout on the pressuretrol at 2psi.
On second look, it appears to be a bunham independence? smaller than an IN7? I guess the single 2" riser is ok according to burnham.. I would have used both. lower the cutout on the pressuretrol to 1.5 and the diff to .5
Add a gauge. I don't see one anywhere in your pics. Preferably something in the 0-3 psi range. You'll also need a 0-30psi gauge to meet code as well.
I'd replace the pressuretrol with a vaporstat and run it at a cutout of 12oz, cutin of 6 oz to start. Make sure you have plenty of main venting.0 -
Is very possible you rad vent needs to be replace, some inner vents are made out of plastic, specially those sold at the big box stores, get yourself some good vents like gortons or hoffmans,
Also those water drips on top of the sight glass are a sign that some oil may be in the boiler and making wet steam so more skimming is needed
0 -
Cleearly the water drops at the top portion of the sight glass is an indicator of oil in the boiler water. That can create all kinds of strange things, especially wet steam.0
-
Yeah I'm defenetly going to do some skimming before I do anything else once it warms up! Tks for all the answers and recommendations.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements