Triangle Tube Prestige Problem
Andy_27
Member Posts: 17
Hi,
Have any of you seen/heard of this problem.
Prestige Solo 175 -- I try and power it on - it goes into power up sequence - displays loading parameters - then shuts down. Display completely blank.
Any Ideas other than new control board -
Thanks
Have any of you seen/heard of this problem.
Prestige Solo 175 -- I try and power it on - it goes into power up sequence - displays loading parameters - then shuts down. Display completely blank.
Any Ideas other than new control board -
Thanks
0
Comments
-
Yep. Just had a 110 do the same thing. Was the OEM power switch. Was able to manipulate it to stay on and replaced it a few days later.0