Flow Check Valve Location.
Thanks Doc.
Comments
-
Generally better to put any restrictions (check valves included) on the pressure side of the circ.0
-
Thanks for the quick reply. I will place BFP on the output side of the circulator.0
-
what model #? Are you referring to the swing check or flow check? I think HTP wants I F E circulators. Copy and post diagram..So many different manuf. and model #s these days.0
-
0
-
Can you tell me what your connecting it to and where you see the flow check
0 -
Currently it's a Bock CT30, indirect water heater. It is connected to a WeilMclain GV4 series 2 natural gas water boiler. In the indirect coil on the RETURN side is a Grundfos UP 15-42fr and the Watts BFP 2000 is siting right on top of the circulator. It's blue on the left in Photo...
http://screencast.com/t/AhmznjCGoVn0
I will be turning the circulator 90 degrees and moving it to the hot side so it's flow will be as shown as in the diagram...
http://screencast.com/t/PUvfGXF0u3rj
So then, I can either place the BFP in front of or behind the circulator.
Thanks for your help.
0 -
Any possibility that that black plastic exhaust vent pipe and fitting is the recalled Plex Vent or Ultra Vent? It looks like it.0
-
Yeah, there is a voluntary recall on that. Apparently many of them cracked from heat and age. I took it out last year, took it apart , inspected and reassembled. You get rebate on your replacement cost for the SS version. I'll see about getting it replaced when the Bock is out of the way. Should be easier working in the area then.
I found out they won't rebate me back the cost unless I have pro do it. So I don't know if I'll have it done or not. Your the 2nd guy to notice it and make mention of it.0 -
Wow From the pic I see there is no way that was installed by an experienced installer…I suggest you get a hold of one…Sorry just my thinking...0
-
Are you talking about the high temp black plastic pipe?
I'm more concerned about the circ and flow check.
0 -
I am talking about the workmanship I see in the pic. Looks like a moonlighter did the work…Sorry, again just being honest...0
-
Nothing to be sorry about.
Yeah, it was a self install with a friend 20 years ago. Conversion from hot air to hot water baseboard. I'm not a pro & not pretending to be one. It's been a great system, even if it ain't so pretty.
So can you share your thoughts on the BFP or are you going to keep me in suspense?0 -
Congrats for moving from forced air! If it's worked for 20 years you must have done something right. Are you talking about a flow check or a back flow preventer?
And JA, this is heating help, not heating criticism. When in doubt, refer to rule #1.
Rob0 -
No, not at all, give me till tomorrow to look at it…..Getting ready for the Pats game..Hopefully not the end of an era...0
-
downstream of the circ is best. Use a properly sized hydronic type check. I prefer the low 1/2 psi "pop" spring check with a tapered cone and soft seat. They look a lot like the check you see in the circs these days.
If you over size a check, like a swing check, they can rattle, as they need full flow to hold them completely open. Stay away from swing and flat disc style checks in hydronic systems.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
UT OH! The Watts flow check valve that's in there now is a RATTLER. Been rattling since day one. It is 3/4" model 2000. Because I was going from 3/4 to 1" I just bought the same kind in the 1" version. Upon looking at it I see it is a flat disc type. So I won't be using that one . I'll go to my local plumbing supply 1st A.M. and get the type you say. Thanks for that tip hot rod.
I'd like to swap out the Bock tomorrow. Don't wanna wait. (Coil Leak)
0 -
Rob , Back flow preventer.0
-
Docfletcher said:
UT OH! The Watts flow check valve that's in there now is a RATTLER. Been rattling since day one. It is 3/4" model 2000. Because I was going from 3/4 to 1" I just bought the same kind in the 1" version. Upon looking at it I see it is a flat disc type. So I won't be using that one . I'll go to my local plumbing supply 1st A.M. and get the type you say. Thanks for that tip hot rod.
I'd like to swap out the Bock tomorrow. Don't wanna wait. (Coil Leak)
Yeah, size a hydronic check to the flow rate, not pipe size. I like the Conbraco brand. Low "pop" and what is called a "bubble free" stop.
Swing, flapper and disc style checks are not "bubble free" shut off typically, so mother nature, with a temperature delta to work with can cause some ghost flow in those style checks.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
61-105-01 Is the closest match to my current flow rate (5.9) and my will be flow rate (8) Thanks all you guys for your help.0
-
The circulator and flow check won't ever kill you.Docfletcher said:Are you talking about the high temp black plastic pipe?
I'm more concerned about the circ and flow check.
That vent pipe can kill you. You've not seen the broken ones that I have.
0 -
I finished indirect install tonight. I do plan to address the high temp plastic pipe issue near term. It's my understanding the issue with them is cracking/chipping/splits at the joints and leaks from improper or poorly applied high temp sealant. For now however suffice it to say none of those are problems with mine. It is in fine shape. I guess that's why I been dragging my feet on getting it done.:) So the indirect is in, and there's no more rattle thanks to Rob's tip regarding a ball cone check valve. All is quiet in the garage.
I want to thank all you guys for taking the time to help me out with this whole indirect heater thing. This is a fine forum.0 -
I think you meant Hot Rod's tip.0
-
Yes I did mean Hot rod's tip. Thanks for the heads up on that.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements