Gorton #1 vent

Tom E_3
Member Posts: 3
Is there any difference in the venting rate between the 3/4" or 3/8" pipe size of the Gorton#1 valve? Thanks
0
Comments
-
Any Gorton #1 will vent at the same rate - 0.3cfm
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Check and see if it is enough for your system.--NBC0
-
What's the venting rate between the gorton 1 and 2???0
-
It takes roughly 3 #1 to equal a #2.0