Efficiency of Nat Gas Steam Boiler
Kjmass1
Member Posts: 243
I have a 1950's Pennco natural gas boiler, I believe 155k btu. One of your pros from this site helped tune it up as it had been neglected with the prior owner.
As of right now it seems to be running great. I was wondering if there is a way I can test efficiency? MA has a $2k rebate to upgrade and I was wondering what the return would be on a newer 84% efficient boiler.
Any way I could figure this out on my own?
Thanks
As of right now it seems to be running great. I was wondering if there is a way I can test efficiency? MA has a $2k rebate to upgrade and I was wondering what the return would be on a newer 84% efficient boiler.
Any way I could figure this out on my own?
Thanks
0
Comments
-
What is the efficiency of that old boiler? What did the pro think about it's condition?
You will have to install a chimney liner with a new boiler if you don't already have one - they don't give them away.
If the old boiler is 70% efficient then your savings would be 14% of your fuel bill, if it's 60% your savings would be 24% of your fuel bill. If it were 70% efficient AND still in good shape you might be better off using the money to upgrade the building it's in.
That old boiler is going to be replaced at some point, make sure your the one who decides when it's in your best interests to do that. Make sure the contractor knows what he is doing, a bargain price on the install isn't worth it if it's not installed correctly.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
Thanks Bob. The plumber thought it was best to keep it for the winter after putting some $$ in to it. It will be our first winter in the house after doing a lot of construction and insulation improvements.
Is the time it takes to make steam from a cold start an indicator off its health? Or the time it takes to travel to the end of the mains on a warm start?0 -
Where does it sat you have to installer a chimney liner , going gas to gas…..0
-
This is what the MA Plumbing board has to say:
http://www.mass.gov/ocabr/docs/dpl/boards/pl/exception-to-lining-an-existing-chimney.pdf0 -
That was my point, no need for a liner if you fall under the guidelines…..Nice post Eric0
-
So I was reading that that you can determine the efficiency of your boiler when it was put in to production by dividing the input by output. So roughly 192k/153k puts it at 78% when it was new. I imagine that has decreased over the years but it is a good baseline. Decades later we're barely at 84% but that is physics I guess.0
-
Remember that the 78% figure was a steady state figure. That is totally different than AFUE used on today's boiler. Odds are something from the 50s has an ANNUAL efficiency of 60% or worse. Annual efficiency looks at how much heat is lost on the warm up of the boiler plus how much is lost on cool down plus up the flue during off cycle. With steam you are limited to mid 80s for AFUE.
With hot water you can get up to about 85% AFUE on a non condensing boiler, beyond that you would need a condensing boiler and the AFUE continues and varies based on water temp. Usually if you have water temp above about 140° you are not condensing and your AFUE is close to that of the standard boiler.
Of course AFUE assumes proper sizing too. If you have an oversized boiler constantly cycling, real world annual efficiency will be well lower than the rating. Like a driver driving his car aggressively won't get the rated MPG either.0 -
Thanks! That is very helpful. Someone came out to look at it for possible replacement and they thought it was a 1970's model...so hopefully it is a little more efficient than that.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements