Which Nozzle to use.
Harvey Ramer
Member Posts: 2,261
in Oil Heating
I have been tasked with repairing this gluttonous hulking dinosaur.
http://www.discountstoves.net/Glenwood-3050-Automatic-Multi-Fuel-Furnace-p/3050gw.htm
The one I am working on is older and does not have the hx fins on the oil combustion chamber. It is rather just a 2' diameter by 2' long round tube that exits into the back of the fire box. I am lining the tube with a wet blanket and patching the cracks with furnace cement. Also I am replacing the oil burner.
Question is, what kind of nozzle might be best suited for this unconventional application? I was thinking of maybe starting with a type B @ 40° to 45° angle.
Harvey
http://www.discountstoves.net/Glenwood-3050-Automatic-Multi-Fuel-Furnace-p/3050gw.htm
The one I am working on is older and does not have the hx fins on the oil combustion chamber. It is rather just a 2' diameter by 2' long round tube that exits into the back of the fire box. I am lining the tube with a wet blanket and patching the cracks with furnace cement. Also I am replacing the oil burner.
Question is, what kind of nozzle might be best suited for this unconventional application? I was thinking of maybe starting with a type B @ 40° to 45° angle.
Harvey
0
Comments
-
What burner are we talking?0
-
AFG Beckett 9" tube.0
-
70 degree is as narrow as I would go on the AFG. This isn't a L or N head? Just the typ F head?0
-
Burner head is L1. Tube assembly is AFG90MB.0
-
Go with the 60 and jack er up to 150 or so and see how it looks. The 45 might impinge?0
-
Thanks Bob. I'll give it a try.
Harvey0 -
Let us know..I had a Tarm rehab once..similar.0
-
@Bob Bona This furnace has no barometric damper. What are your thoughts on that? I know oil should have one but what about the wood?
Harvey0 -
Getting above my pay grade Harvey My first thought is I can see the oil draft be damned in the interest of proper wood draft?0
-
-
And if you install a barometric damper like a Field RC on the flue. you should see how red the pipe can get when you get a chimney fire. You hear that jet engine roar in the chimney, you go outside and look up at the chimney, and think that a V-2 Rocket went down the chimney.captainco said:Wood furnaces and boilers usually require a -.05"W.C. draft at the outlet. The draft for oil will be what it will be. Excessive draft makes the wood burn to fast and low draft smokes up the house.
0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements