Last radiator on the line is cold to luke warm

Boiler was install before the new owner moved in (25 yrs ago) and the last room was always cold.
Install the main vent valves correctly and calculated and air in the main is vented and steam around 3.5 to 4 minutes
Size each radiator vent valves accordingly to there size ( aero convector radiators) total EDR 292 Boiler cap. 440 sq.
Still the last radiator on the main pipe the riser is also luke warm
try adding several vent valves for faster bleeding of the air no change.
Wondering if the near piping on the Weil Mclain E6 boiler is causing my last radiator to be luke warm?
See attach photo

Comments

  • mercedes
    mercedes Member Posts: 67
    Bob

    Will recheck the slope of the last radiator piping from the main pipe this morning
    running at 1.5 psi cutout
    cut in .5
    I am using Dan Holohan "Greening Steam" chapter 6 venting practice and using gorton valves #4 and #5, main vent 2 #2
    Before last winter 2013 I changed the vent valve and the rooms got more uniform in heat but the last radiator is still luke warm.
    Will do near piping but trying to calculate some room as they built very tight to the boiler area.

    Thank you for your help.
    Dan
  • BobC
    BobC Member Posts: 5,502
    If you can get someone to help you try this test. Remove the vent from that problem radiator. Set the thermostat well up so it won't turn things off quickly and have some stand next to the boiler ready to kill it's power if steam starts to come out of the vent tapping..

    See if the radiator gets hot and if not how close the steam gets to that radiator.

    If it never gets hot you are either collapsing steam at a furious rate or maybe the radiator valve is broken and the valve is stopping the steam flow. If air is being trapped by a blockage the steam will never flow beyond it.

    Also do both mains seem to be heating up at about the same rate?

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • mercedes
    mercedes Member Posts: 67
    Bob

    I will try this method. Will tell you of the results. I never thought about the steam valve for the radiator maybe internally the valve is partially closed. Good idea. Will follow the steam heat and how far it goes.

    thanks
    Dan