Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

NYC BOILER CODE

ANY ONE KNOW RULING ON HARD WIRED CARBON MONOXIDE DETECTOR CONNECTED IN SERIES WITH BOILER CIRCUIT. IN 10 GAS FIRED 315,000 BTU 100 GAL. GAS FIRED WATER HEATER. JOHN FROM GATEWAY PROBABLY WILL KNOW ALL ABOUT THIS ISSUE. bob young nyc lic. plbr # 685

Comments

  • JohnNY
    JohnNY Member Posts: 3,293
    Hi Bob. I'm sorry I didn't see this much sooner.
    Perhaps you've worked this out by now, but the "official" word I've gotten from the DoB is that interlocked CO detectors were to be installed "at the inspectors' discretion". So far, every place we have a boiler inside an apartment, as opposed to in a cellar or roof or mechanical room located outside of "living space", we are required to install the CO detector and boiler relay.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • bob young
    bob young Member Posts: 2,177
    THANX, JOHN. BOB DALY GAVE ME THE ANSWERS I NEEDED. A REAL GENT. MET HIM A FEW YEARS AT A CONTINUING ED. SEMINAR.