NYC BOILER CODE

ANY ONE KNOW RULING ON HARD WIRED CARBON MONOXIDE DETECTOR CONNECTED IN SERIES WITH BOILER CIRCUIT. IN 10 GAS FIRED 315,000 BTU 100 GAL. GAS FIRED WATER HEATER. JOHN FROM GATEWAY PROBABLY WILL KNOW ALL ABOUT THIS ISSUE. bob young nyc lic. plbr # 685

Comments

  • JohnNY
    JohnNY Member Posts: 2,738
    Hi Bob. I'm sorry I didn't see this much sooner.
    Perhaps you've worked this out by now, but the "official" word I've gotten from the DoB is that interlocked CO detectors were to be installed "at the inspectors' discretion". So far, every place we have a boiler inside an apartment, as opposed to in a cellar or roof or mechanical room located outside of "living space", we are required to install the CO detector and boiler relay.
    Contact John "JohnNY" Cataneo, Master Plumber
    in New York
    in New Jersey
    for Consulting Work
    or take his class.
  • bob young
    bob young Member Posts: 2,177
    THANX, JOHN. BOB DALY GAVE ME THE ANSWERS I NEEDED. A REAL GENT. MET HIM A FEW YEARS AT A CONTINUING ED. SEMINAR.