Landon Radiators

Options
Hi Everyone I was out looking at a steam boiler replacement today and came across these radiators in the house. It Says Landon above the top plug. I can not find this radiator in the EDR book and was looking for some help.

Thanks

Comments

  • gerry gill
    gerry gill Member Posts: 3,078
    Options
    humm, doesnt look like a tube radiator, more like a flue radiator which usually had more edr per section. How tall is it?
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Steamhead
    Steamhead Member Posts: 16,842
    Options
    It's a large-tube radiator with the spaces between the tubes filled in. Any standard large-tube chart such as American Corto, National Aero or Weil-McLain Cameo should be fine.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    BTU
  • Michael Welch
    Michael Welch Member Posts: 43
    Options
    I have a total of 12 of these radiators on the job ranging from 20 inches high to 38 high. I was thinking the same thing that the filled in area might give it more EDR.