OK to use 45-degree elbow to raise the steam vent?

agurkas
Member Posts: 238
I want to put in #2 Gorton, but I don't have enough room, if I am doing a straight shot up. Thinking about putting 45 degree elbow. Any issues with that setup?
0
Comments
-
The vent has to be vertical. The pipe leading to it can be angled as long as it can drain. Don't want to form a p-trap or the vent will stop working. Not sure if that helped you?gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Does it have to be at 90 degree angle to the main?
I guess then I need to do 45 from the main, then a nipple, then another 45 and that should put the vent at 90 degrees to the main.0 -
That's picture perfect Mark!gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Such clean install. Nothing in my plumbing looks anything like that.0