Some help with sq.ft and boiler recommendation please
PaulC
Member Posts: 9
I currently have an oil fired steam boiler. I'm piped in and converting to gas. The current oil burner is a peerless. It's gross output is 179k steam, net is 550 sq.ft steam, IBR 134k btu/hr steam. It was also used for domestic hot water, but that has already been switched over to a hot water heater
I have 5 single feed radiators and 31 linear feet of cast iron baseboard. 2 baseboards are single piped, one has a feed, and return.
My calculations are 156sq.ft on the radiators, based on information charts from this web site I don't know how many sq.ft. to use for the baseboard.
The radiators are as follows:
1) 7 3/8"w 23"h
2 large tubes, 12 sections
2)4 3/4" w 23"h, 4 thin tubes, 26 sections
3&4) 4 3/4"w 25"h, 4 thin tubes, 12 & 18 sections
5) 3 1/2w 25"h, 3 thin tubes, 10 sections
The baseboard is 7" h, 2 1/2w, 31linear feet.
I've had 2 estimates, reasonably close in price.
One contractor used the information I gave him, he calculated 452-480 sq.ft. He also forwarded the info to his distributor, they agreed on a w.McClain 5500 200k btu. input, 167k btu output. I also gave him the info on the existing peerless.
Another contractor just read the info on the existing. His unit recommendation is a w. McClain 120k btu, 83% AFUE gas fired steam boiler.
Does anyone have any thoughts on these recommendations?
I have 5 single feed radiators and 31 linear feet of cast iron baseboard. 2 baseboards are single piped, one has a feed, and return.
My calculations are 156sq.ft on the radiators, based on information charts from this web site I don't know how many sq.ft. to use for the baseboard.
The radiators are as follows:
1) 7 3/8"w 23"h
2 large tubes, 12 sections
2)4 3/4" w 23"h, 4 thin tubes, 26 sections
3&4) 4 3/4"w 25"h, 4 thin tubes, 12 & 18 sections
5) 3 1/2w 25"h, 3 thin tubes, 10 sections
The baseboard is 7" h, 2 1/2w, 31linear feet.
I've had 2 estimates, reasonably close in price.
One contractor used the information I gave him, he calculated 452-480 sq.ft. He also forwarded the info to his distributor, they agreed on a w.McClain 5500 200k btu. input, 167k btu output. I also gave him the info on the existing peerless.
Another contractor just read the info on the existing. His unit recommendation is a w. McClain 120k btu, 83% AFUE gas fired steam boiler.
Does anyone have any thoughts on these recommendations?
0
Comments
-
A few thoughts
A few thoughts:
1) I'm getting roughly 305 sqft., but I'm admittedly taking some liberties as your dimensions don't seem to EXACTLY match any EDR charts I have at a glance (198.76 sqft. for the (5) radiators, and 105.4 for the cast iron baseboard).
2) Anything over this number seems to be over-sized, in other words, 452-480 sqft. seems over-sized.
3) If the second contractor only used the existing boilers specifications, they don't care enough to install the appropriately sized boiler, and therefore, their estimate should be dismissed.
Where are you located?0 -
Some help please
I'm located in Monmouth county in NJ. The peerless was probably installed in the mid 60's. It was probably a replacement from an earlier boiler. My home is over 100 years old. It originally had coal. I had suggested that it was probably oversized, but he ( the first contractor) didn't really respond to that statement. I was not impressed with the second estimate, even though it was lower.0 -
Some Help Please
Ok, obviously my calculations were off. I think I used an old chart, & misunderstood some things. #1 is 2 column. Also, do you add any sq. ft. For piping?0 -
Jstar
Please do the right thing for your system and call Jstar.
He will do what is best and is the only one in NJ I'd trust to work on my system.
Here is his info :
Joe Starosielec
732-494-4357
j.star@thatcherhvac.com
http://thatcherhvac
http://facebook.com/thatcherhvacSingle pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Piping
is already accounted for in the IBR, but your piping losses might exceed this allowance if the pipes aren't insulated.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Some Help please
Yeah, the pipes aren't insulated anymore.
I know the system needs a bit more attention than just a replacement boiler.0 -
Some Help please
Hi Chris, thanks. Have they done work for you? How did you find them?0 -
Yes
Joe did some custom wiring for me when the Ecosteam system was installed.
I found Joe on here and have seen a lot of his work.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Recommendation
Joe is a little too far from me to call him for service, but I wanted to say how impressed I've been with the way he understands steam. He not only has tons of experience, but he's clearly spent a lot of time studying the physics involved. As someone with a science/engineering background I'm not easily impressed, but the knowledge he displays in this forum never ceases to amaze me.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Advantages of this forum
If you click on Joe's name, you will get a list of all of his postings on this site.
If you read a number of them, you will understand that he is a true steam expert, who is also a good communicator.
You would be better served getting this job right, done by someone with easily verified talents, rather than choosing someone else who may be a shot in the dark.--NBC0 -
Some help please
Thank you all for your input. Any other thoughts are still welcome. I did call Joe, and have an appt with him next week.0 -
To iterate
When I was reading the post and saw that you were in N.J. I was going to recommend Joe. Chris beat me to it though. Joe will probably not be the low bidder however you don't get what you don't pay for. Have it done once and have it done right.
JMHO,
Rob0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements