Embassy Industries Onex Boiler FILL issue

dazonex
Member Posts: 2
in Gas Heating
I have an Embassy industries Onex Boiler and the screen says FILL. i cant seem to get the boiler started. the psi is correct and the boiler is filled with water.
0
Comments
-
If the boiler....
is filled and pressurized w/ water and you are still getting the fill readout then the pressure sensor is plugged w/ junk. I have run into this a number of times in the last 3 months on these boilers I have in the field. You can do 3 things. Jump out the sensor temporarily... replace it or clean it out1 -
I had the FILL code on my Onex Boiler and it turned out to be the pressure sensor switch that was indeed "plugged with junk" It was a simple fix after I knew what the problem was. I talked with 4 to 5 plumbing experts and not one suggested the pressure switch. kcopp nailed it.0
-