I don't have 18"
h12721aa
Member Posts: 17
I am installing a new boiler and have some problems with dimension.
1)
1 1/2" piping coming from the boiler system supply in to the Air Scoop. there should be 18" of horizontal pipe witch i don't have.
2)
Between the supply and the return I should put a 1 1/2" by pass valve. With two Ts and the valve I don't know if that will fit in 5". Must the By Pass Pipe also 1 1/2" or can I go smaller ? The boiler is a Burnham MPO-IQ 84 for two Zone and water heater.
The print shows 1 1/2" pipe lay out.
What to do? going around in loops or what ?
Hilmar
1)
1 1/2" piping coming from the boiler system supply in to the Air Scoop. there should be 18" of horizontal pipe witch i don't have.
2)
Between the supply and the return I should put a 1 1/2" by pass valve. With two Ts and the valve I don't know if that will fit in 5". Must the By Pass Pipe also 1 1/2" or can I go smaller ? The boiler is a Burnham MPO-IQ 84 for two Zone and water heater.
The print shows 1 1/2" pipe lay out.
What to do? going around in loops or what ?
Hilmar
0
Comments
-
Air scoop or eliminator
The 18" rule is a good one to be thinking of but not so important if you have a modern air eliminator as opposed to old style air scoop . Which do you have there ? Send a picture or 2 .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
what size boiler?
If that is a 64,000 BTU/ hr hot water boiler you could use much smaller pipe, check with the installation manual but 1" pipe should easily move 6 gpm or so.
1-1/2" pipe needs around 11 gpm flow rate to assure 2 feet per second. You want 2-4 fps to be able to push or pull the air around the piping loop.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I don't have 18
Hi Rich and hot rod
This is a reply to the question. I don"t have a picture of the air scoop look at the print.
A Table calls for a flow rate of 4.5 Gal/Min for the MPO-IQ84 = 64000BTU.
Hilmar0 -
Pipe Sizing
One inch is fine for 4-9 gpm. A spiro-vent has none of those piping restrictions.0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements