Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Beckett NX

Options
Jesse322
Jesse322 Member Posts: 1
What does the NX burner usually run for co2

Comments

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,541
    Options
    CO2

    Whatever you set it to! Will run 14% plus at zero smoke but that doesn't leave a lot of safety margin! 12.5-13% is a safe number.
    To learn more about this professional, click here to visit their ad in Find A Contractor.