Beckett NX

Jesse322
Jesse322 Member Posts: 1
What does the NX burner usually run for co2

Comments

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,563
    CO2

    Whatever you set it to! Will run 14% plus at zero smoke but that doesn't leave a lot of safety margin! 12.5-13% is a safe number.