Current relay/potential relay
Harvey Ramer
Member Posts: 2,261
How best to test these miserable critters while the compressor is dry docked? Don't want to be wasting any start caps.
Harvey
Harvey
0
Comments
-
Checking PMRs and CMRs
Checking a Current Magnetic Relay:
Take a resistance reading across the coil on the relay (usually terminals L and M) - The resistance of the coil should be less than 1 ohm or so.
Position the CMR in its normal position (coil at the bottom) and check for continuity across the contacts of the relay (Terminals S and L). This reading should be infinite. Now, with the meter's leads still connected to S and L, turn the relay upside down. You should now read continuity. This indicates that the contacts are moving freely within the relay.
If the coil and the contacts check out, the relay is good.
Checking a Potential Magnetic Relay:
Take a resistance reading across the coil (terminals 2 and 5) on the relay - The resistance of the coil should be very high. This resistance varies from manufacturer to manufacturer, but readings well above 1000 ohms are common.
Next, check for continuity across the contacts of the relay (Terminals 1 and 2). This reading should be zero or very close to zero.
If the coil and the contacts check out okay, there is still the possibility that the relay is not functioning properly. You still need to check whether or not the contacts open when the "pick-up" voltage is reached. The pick-up voltage is the voltage at which the contacts will open, and is much higher than the line voltage that is supplied to the unit.
I hope this helps!There was an error rendering this rich post.
0 -
Pot Relay
.I always visually check the contacts of the Potential Relay. The new PR is easy to gain access to the contacts, the older PR has a screw on the backside ,under a piece of dried up rubber.0 -
It certainly does.
Thanks for the help guys!!!
Harvey0 -
Very rare
For that relay to go bad. If the comp is locked you can always piggy back a booster on the run capacitor. If relay is working it is taking out the start winding. Keep in mind with no power to the start winding it will give you the reading on your meter like a locked comp would.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements