Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
STEAM BOILER W/ INDIRECT help !!!!
bob young
Member Posts: 2,177
REPLACEMENT STEAM BOILER .ea too confined for independant water heaters. not familiar with sizing method to provide indirect domestic tank , etc. 14 families. need formula for additional btu load to add to steam boiler. thanx, bob nyc
0
Comments
-
We need some info
John Barba had a nice webinar on sizing an indirect.
I suggest you view it.
For the formula to find out how many gallons of water your going to use go to hot water.com
If you want tankless then see me0 -
IDT
I would be cautious about adding any BTUH's to the steam boiler. You'd be surprised at just how effective an indirect tank will be, even at lower input BTUH's.
At 14 showers, I would look for a First Hour Rating of 240. If your total BTUH's are close to 200K, you'll be fine not adding any extra.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements