What? How come?

Techman
Member Posts: 2,144
Working on a regular AC system (RTU , new to me) my cohort said "we have 216v ,L1 to L2 .BUT, BUT we have 123v to ground L 1 & 123 V to ground L2! What What? How How come???
0
Comments
-
3ø Wye System
With a tad of imbalance (should be 213V L-L if all is well.)0 -
electrician time
How is it wired in breaker box? Do you have 220 there?0 -
What?
Our measurements were at the AC unit disconnect. Do not know what is at the CB panel.0 -
I thought you were posting another quiz
In a three phase wye system, line to line voltage is equal to the √3 times the line to neutral voltage.
123V line to neutral times 1.732 = 213 V line to line.
Slight variations can be caused by nonlinear loading or the use of a DVM which does not measure true RMS AC.0 -
Voltages.
Truth be told , I'm asking for a fellow wallie ! He didn't want to ask! Shame on him!!!!Your welome!
SWEI- Thanks! I know about that stuff ,but I don't know about that stuff . Know what I mean?0
Categories
- 120.3K All Categories
- 83.6K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 414 Carbon Monoxide Awareness
- 30 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.6K Gas Heating
- 114 Geothermal
- 152 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 736 Plumbing
- 5.2K Radiant Heating
- 357 Solar
- 13.8K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 36 Industry Classes
- 70 Job Opportunities
- 14 Recall Announcements