Steam Boiler

4Johnpipe
4Johnpipe Member Posts: 485
I'm looking for a fan assisted steam boiler. The one supplier I reached before closing today said they have no such product. Has anyone on this site heard of or use one that is recommended?
LANGAN'S PLUMBING & HEATING LLC
Considerate People, Considerate Service, Consider It Done!
732-751-1560
email: langansph@yahoo.com
www.langansplumbing.com

Comments

  • Steamhead
    Steamhead Member Posts: 17,323
    Couple more questions

    Oil or gas?



    What size?



    Why do you need fan-assist (adds complication and more service calls)?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    Fan assisted boiler

    Are you maybe thinking of a power burner in a wet base boiler?--NBC
  • 4Johnpipe
    4Johnpipe Member Posts: 485
    Questions

    I am looking for a natural gas boiler 187K BTU's input. The issue is the existing chimney is collapsed or collapsing. The building is old and poorly insulated.
    LANGAN'S PLUMBING & HEATING LLC
    Considerate People, Considerate Service, Consider It Done!
    732-751-1560
    email: langansph@yahoo.com
    www.langansplumbing.com
  • Steamhead
    Steamhead Member Posts: 17,323
    If the chimney just has a bad lining

    and the structure is otherwise OK, the best bet would be to have it lined with stainless steel. This does not add any moving parts to the installation that will cause trouble down the road.



    If the basic structure of the chimney is failing, I'd still have it rebuilt and properly lined even though that would probably cost more. The reason is the same- fewer moving parts requiring service. Who needs to have to respond to a 1:00 AM no-heat call caused by a bad power vent?



    But if you absolutely have to abandon the chimney, there is only one gas steamer with built-in power venting I know of- the Burnham Independence. Unfortunately, we've replaced a lot of Independence boilers in the last several years due to rotting out above the waterline- I'm not sure if this is because of a problem with them, or simply because there are so many more of them.



    If the existing boiler is in good shape, Field and Tjernlund both make power venters that you can use with it. These come with safety interlocks that MUST be wired in correctly to avoid CO getting into the building.



    Also be aware that there are limits to where you can exhaust a sidewall-vented boiler, such as clearances above snow lines and from doors and windows. The place to start is whatever Gas Code is used in your area, possibly NFPA 54 or the International Gas Code. Some places also restrict where you can exhaust such a boiler with respect to property lines.



    If this sounds like a lot- it is. That's why I like chimneys.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,362
    Burnham IN PV

    Power vented steam boiler side wall vented. Of course with a Fields power venter all boilers can be side wall vented.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating