Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Corroded Boiler part?

lowwater
Member Posts: 41
I have a Weil-McClain cg-25-spdn boiler which works fine. Upon annual
cleanup (which I always do) I noticed this part corroded which I believe is the automatic vent. Is it normal and I should have this replaced? What are your thoughts? Much appreciated!
cleanup (which I always do) I noticed this part corroded which I believe is the automatic vent. Is it normal and I should have this replaced? What are your thoughts? Much appreciated!
0
Comments
-
Most definitely
have that vent replaced. I think that's a Maid-o-Mist- there are better ones out there.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements