Honeywell Oil Burner Control
Cradiuss
Member Posts: 1
My oil burner uses Honeywell R8184N 1009 Control. Can I use Honeywell R8184G 4009 Control? Do I need to make any modifications?
0
Comments
-
nope....and get the right control
I think you have an 8184M, not NThere was an error rendering this rich post.
0 -
The R8184M
has a transformer which is used to operate air-conditioning control circuits. So if this burner is used on a furnasty with central air, you need something to take over that function.
There are two inherent drawbacks to the R8184 control series: 1- most models have a 45-second trial for ignition, which is way too long and can allow "puffbacks" to happen if ignition is delayed, and 2- they do not cut off the ignition spark after the burner has started, which wears out the electrodes prematurely and can cause delayed ignition.
Beckett, Carlin and Honeywell all offer electronic controls that can replace an R8184 and upgrade to a 15-second trial for ignition, and which will also cut off the spark once the burner has started. I would use one of these rather than another R8184. I believe all three manufacturers offer transformer kits that can power your A/C controls too.
And I strongly recommend you have a pro do the upgrade.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements