Do I need to worry about having straight lengths of pipe going to and from low loss header. I know that one likes to put 10 x the pipe diameter in length in front of a pump intake to reduce turbulence. Any general rules for low loss headers. I have limited space. Thanks all
0
Comments
-
A hydro separator?
Size the unit for the maximum flow rate, and the piping for a flow velocity of 4 fps or less. You can close couple to the tank style hydro separators, I have seen ells connected right to the separators.
The separator itself becomes the "wide spot" in the piping and will allow flow velocity to decrease as it enters.
Typically a hydro separator body will be three times the diameter of the piping connected to it, this provides the "low pressure" zone. which in turn provides hydrailuc, air, and dirt separation.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0