Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
taking a hot water zone off of a steam boiler
plumberguy
Member Posts: 1
hi guys looked at a job this week ,somebody took a zone of hydronics off the condensate side of a steam boiler . the apartment that has no heat is piped below the waterline of the boiler. when i got there the oo7 circ. was smoked so i changed it. opened the return to purge the systen and i had no water?noiced the supply and return both had purge valves?
0
Comments
-
Assumptions
At some point air got pumped into the zone. Since it is not pressurized, there is no way to get the air out. Use garden hoses to power purge it. This will deal with the issue at hand, not the ongoing problems it will have.0 -
You Should Use
A Stainless Steel or Bronze circulator, not a regular 007.
Thanks, Bob GagnonTo learn more about this professional, click here to visit their ad in Find A Contractor.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements