biasi b-3

Eric_51
Member Posts: 30
in Oil Heating
is the biasi b-3 big enough for a house that calls for 46,000 btu with indirect hw with priority set?
0
Comments
-
Most likely.....
If you did the heatloss and your hot water needs are not crazy.0 -
Yes
Yes,the 63K is well over the 46K heat loss. How did you calculate the 46K? Every HL program has tons of fudge in it, I bet the real HL is 30K or lessTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
slant fin
I used slat fins after i posted about the discrepancies in the calculators. i ordered the boiler yesterday just waiting for it to show. then just have to figure the how i want my zones to go and what controls to run. its so confusing going with this new stuff, if i just put it in like the old it would be easy but a waste of time and money..0