Richardson system
lbud
Member Posts: 3
I ran into a Richardson main vent that is broken. The screw is broken off of the diaphragm. There are two of these on the system at the ends of the returns before they drop down. One side of the system is working, the side with the broken vent is not. There are no traps on the radiators. The supplies go to the top of the radiators and the condensate rolls out of the bottom on the other end. I believe this system is supposed to operate on very low pressure. The boiler has a standard PA404 control that I turned down as far as it will go but I want to change it to a vapoprstat.
Will a Hoffman #76 Vacuum Vent work on this system?
If not what is recommended?
Will a Hoffman #76 Vacuum Vent work on this system?
If not what is recommended?
0
Comments
-
Richardson
This vapor system should not operate above 5 ounces of pressure. 3oz should be your cut-out. A Vaporstat is a necessity here.
I would install a bunch of Gorton 2's or thermostatic traps on the returns for venting.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements