Risers
Pughie1
Member Posts: 135
Hi Guys,
Just wondering what your guys take on using one riser instead of two. The job I am looking at has just one riser in use even though the boiler in question has provisions for an additional riser. In the manufacturers instructions they say that for this model one riser is acceptable. I've run the velocity calculations and it does fall within acceptable guidelines (Lost Art charts). However, just because its OK doesn't mean you HAVE to do it that way. I've always been of the belief that "if they give you two - USE UM"!. I just feel it gives you a More even distribution of the steam as it leaves the boiler. Years ago we were loosing the section opposite the riser (on this model by the way) on some installations. In the "Lost Art" Dan describes what I thing was going on. Just my 2 cents.
John Pughe
Just wondering what your guys take on using one riser instead of two. The job I am looking at has just one riser in use even though the boiler in question has provisions for an additional riser. In the manufacturers instructions they say that for this model one riser is acceptable. I've run the velocity calculations and it does fall within acceptable guidelines (Lost Art charts). However, just because its OK doesn't mean you HAVE to do it that way. I've always been of the belief that "if they give you two - USE UM"!. I just feel it gives you a More even distribution of the steam as it leaves the boiler. Years ago we were loosing the section opposite the riser (on this model by the way) on some installations. In the "Lost Art" Dan describes what I thing was going on. Just my 2 cents.
John Pughe
0
Comments
-
Risers
I always double a 2" riser. If it's 3", on smaller models, I'll only use one. As long as the velocities are within acceptable limits and the pressure is very low (ounces), we've had no problems with it. We just make sure to always use the riser on the same side as the gauge glass. The extra riser opening is a great place for a Vaporstat.0 -
Risers
Thanks for replying, Glad to get your opinion.
John0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements