LWCO SafeGuard problem
xcinek
Member Posts: 14
Here is my problem hope someone can help.
I have a
Burnham IN8
Safguard Model 450
VXT-120
Pressure Set to Cut In 1.5 PSI
Cut out 1.0 PSI
Here is my problem.
When my burner runs for a longer period of time the Safguard does not shut off the system but the secondary cutoff kills the system and it doesn't turn on until i rest it.
I have cleaned the probe. I did the test and the the Safguard 450 works but looks like not all the time.
The settings on it I have wait 2 minutes and add 2 gallons of water in case of low water condition.
Any reason or how to check that the Safguard is in good working order.
I have a
Burnham IN8
Safguard Model 450
VXT-120
Pressure Set to Cut In 1.5 PSI
Cut out 1.0 PSI
Here is my problem.
When my burner runs for a longer period of time the Safguard does not shut off the system but the secondary cutoff kills the system and it doesn't turn on until i rest it.
I have cleaned the probe. I did the test and the the Safguard 450 works but looks like not all the time.
The settings on it I have wait 2 minutes and add 2 gallons of water in case of low water condition.
Any reason or how to check that the Safguard is in good working order.
0
Comments
-
The real problem
Your system seems to be returning water very slowly, causing a plunging waterline, and triggering the LWCO. It should be able to run more or less indefinitely without showing any appreciable drop. How long does it take for the water level to come back to normal?--NBC0 -
.
yea but the should the first low water cut off cut out the system and not the 2nd one kill the system. then add water if it senses low water level ?
My return lines are old I will replace them this year but have to wait till summer.
Once I add adequate water level the system will run for a week or 2 and the once the water goes lower right but Low water level then it happens.
Well my system has been runun more then usual since NY had very cold past 2 weeks.0 -
.
I have done near boiler piping from 2 inch to 4 inch lowered my pressure so the system runs much smoother not to much water bouncing.
but still now the low water cut off
this is 2 year old boiler give me such a head ache0 -
Where is the water going?
I think the real question is where is the water going, if the level drops that much in a week or two to trip it at all? I'm sure clogged returns aren't helping the situation, but then you'd always see this problem. Since it goes away for a couple of weeks when you addwater, it may be a leak.
I have know idea why the secondary probe works as the trigger.Two-pipe Trane vaporvacuum system; 1466 edr
Twinned, staged Slantfin TR50s piped into 4" header with Riello G400 burners; 240K lead, 200K lag Btus. Controlled by Taco Relay and Honeywell RTH6580WF0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements