Delta t on radiant

cph_3
cph_3 Member Posts: 5
How

Can I

Slow down the water going through my tubing so I can get a wider delta t

I have a small bathroom that i put in radiant heat about 170 feet of tubing

I used a three way mixing valve and a taco 007 circ my water supply is 125 and

My return is 118 I want to put a gate valve in to throttle down the flow but I do

Not know if I should put it on the supply or return any suggestions

Comments

  • hot_rod
    hot_rod Member Posts: 23,047
    Why?

    do you want a wider ∆T? Sounds like maybe too much circ for one 170' loop? Consider sizing down the pump, if you must shed away head energy use a globe or a specific balance valve. Closing down a gate valve enough to force that circ to run down may cause some noise and other un-desireable effects.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream