Need boiler sizing help
I could use some of your collective experience checking my boiler sizing calculations:
Cubic square feet 150,000 (csf x 6 on main, csf x 6 on 2nd, .5 of that in basement)
=150,000 btu output needed
X 1.15 (15%) make up for piping
X 1.15 (15%) pick up
=198,375
X 80% efficiency of boiler
=238,050 btu boiler size needed
Radiators:
Room height depth columns width sections
livings 20 8 5 81 33
livingn 20 8 5 50 21
dining 20 8 5 77 32
kitchen 32 8 5 35 15
master 20 8 5 68 28
bath 20 8 5 35 15
guest 20 8 5 63 26
nbed 20 8 5 68 28
sbed 20 8 5 50 21
Does 238K look correct?
  • Mark N
    Mark N Posts: 1,148
    edited January 2014
    EDR
    Figure out the EDR of your rads. Then choose the boiler based upon that number. Post some pictures of your rads. I believe your rads are 2.66 sq ft per section.
  • EzzyT
    EzzyT Posts: 1,380
    edited January 2014
    238k is to much
    Your looking at 582.5 square feet of steam.
    582.5x240= 139,800 btus that's your net IBR. The boiler manufactures all include the pick factor on there boiler so no need to add that in.
    You need 193,000 btus
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • mcdave2
    mcdave2 Posts: 12
    radiator photo
    Dining room radiator photo attached
    Thanks.
  • mcdave2
    mcdave2 Posts: 12
    dining radiator photo
    attached
  • mcdave2
    mcdave2 Posts: 12
    new boiler size
    So the boiler i am looking at is a New Yorker with IBR rating of 629 sq ft of steam and btu of 151000/hr with a heating cap of 201000.
    So I am concluding that while is slightly oversized it woiuld be appropriate for my home?
  • mcdave2
    mcdave2 Posts: 12
    boiler spec
    here is the tag from the boiler
  • mcdave2
    mcdave2 Posts: 12
    tag
    tag