condensate problem in school

I work in the maintenance dept of a school system.One of the high schools has 2 cleaverbrook 350 hp firetube boilers and along with it a boiler feed tank to recieve the condensate.The feed tank has 3 inlets to it, 1 main,1 smaller main from lockroom and aux gym, and 1 from a condensate tank(pumped) 400-500 feet away that does upper industrial art wing.The problem is that at nite the vent at boiler feed tank is ripping steam or flash steam into the boiler room.any ideas?

Comments

  • soak123
    soak123 Member Posts: 2
    edited January 2014
    BTW

    the steam traps have all been rebuilt 2 -3 years ago
  • Pumpguy
    Pumpguy Member Posts: 693
    The only way...

     steam can get into your boiler feed tank is past a bad trap out in the system, or possibly past a bad check valve on a boiler feed pump. 



    Typically, boiler feed pumps discharge into the boiler below the water line, so that's not very likely. 



    I suppose it's possible there's a steam leak across an equalizer line between the steam header and return line.  Again, not very likely because that leak would cause steam in the return line all the time. 



    Now, if your steam header pressure is high enough to allow the condensate to flash back into steam on the return side, that's also a possibility, but not very likely unless your operating at excessively high steam pressure. 



    Traps don't last forever.  Something to keep in mind.



    Hope this helps.
    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
  • JStar
    JStar Member Posts: 2,752
    Steam

    Are you using steam to make hot water through a heat exchanger?

    What pressure are you operating at?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,470
    Traps

    Most likely bad traps. If your steam pressure is high you could get flash steam back at the boiler feed tank.

    Either way the high condensate temperature will kill your feed pumps and pump seals if not fixed