3 questions
remodel
Member Posts: 68
1) Is it worth it to put in a smaller boiler pump and smaller system pump? Boiler a loch 155. Right now I have about 8gpm to the system and 8gpm to boiler all zones calling. One zone calling I have 4 gpm -5gpm to system and 8 gpm at boiler. At 30%-50% fire boiler DT good, at 20% - 7 degree DT. System oversized by 25% so might be a moot point.
2) Can I put cast iron rad/panel rads in place of fin tube BB at the end of my series loop or will I rob too much heat? I would have to pipe it in series and this loop has one FCU off of monoflows right after rad replacement. The remove and replace is about 50%-60% of the 1st floor emitter length.
3) Is negative DT alright at start-up?
2) Can I put cast iron rad/panel rads in place of fin tube BB at the end of my series loop or will I rob too much heat? I would have to pipe it in series and this loop has one FCU off of monoflows right after rad replacement. The remove and replace is about 50%-60% of the 1st floor emitter length.
3) Is negative DT alright at start-up?
0
Comments
-
sorry got posted twice
sorry got posted twice0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements