Johnson Controls Pressuretrol
cwaz
Member Posts: 22
Hello all,
I am looking for some advice on the Johnson Controls pressuretrol that is currently set up on my WM P-SGO-3 (oil fired steam boiler). The lowest pressure I have been able to get the system to operate at is 4.5psi ( I attached a 0-5psi gauge to better trouble shoot), which I thought was way too high for the sake of vents, fuel efficiency, etc, If I dial the cut out on the pressuretrol any lower it will not cut back in and allow the boiler to fire again. I attempted to find manual for the pressuretrol in hopes of figuring this out, but have been unable to do so. A search on the great inter web barely has any info. I would love any input on how to lower the operating pressure of my system. Thanks in advance.
I am looking for some advice on the Johnson Controls pressuretrol that is currently set up on my WM P-SGO-3 (oil fired steam boiler). The lowest pressure I have been able to get the system to operate at is 4.5psi ( I attached a 0-5psi gauge to better trouble shoot), which I thought was way too high for the sake of vents, fuel efficiency, etc, If I dial the cut out on the pressuretrol any lower it will not cut back in and allow the boiler to fire again. I attempted to find manual for the pressuretrol in hopes of figuring this out, but have been unable to do so. A search on the great inter web barely has any info. I would love any input on how to lower the operating pressure of my system. Thanks in advance.
0
Comments
-
Check the pigtail under the pressuretrol
to see if it's plugged up. This can cause your symptoms. I usually blow into the pigtail, but that doesn't taste so good.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Clean as a whistle
The pigtail was clean, shot some compressed air for good measure, but there was very little buildup. It still ran: cut in 1, cut out 4.5, which is not even close to what is set on the pressuretrol.0 -
Then
you need a new pressure control. If that were mine I'd spend the extra money for a Vaporstat. You really don't need more than a pound anyway.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Reccomendations
I figured that was my next step. I can't even get the listed manufacturer (Johnson controls ) to give me any info on it so I'm sure it's probably older than the kid I talked to on the phone. Any suggestions on which model of vaporstat would best suit my needs?0 -
L408J1009
maxes out at 16 oz- 1 pound.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements