Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Size of main vents required
cdm
Member Posts: 77
I have a one pipe system with 1.22 cu.ft. of volume in the 1st main and 1.89 cu.ft. of volume in the second main. I want to REALLY quickly vent both mains in a few minutes - how much venting do I need @ 1oz.? Gortons or Hoffmans ?
thanks -cdm-
thanks -cdm-
0
Comments
-
Gortons
The Hoffman 75 vents at 0.5cfm , the Gorton #1 at 0.33cfm, and the Gorton #2 at 1.1cfm -all at 1 oz. What kind of vents are on there now?
It sounds like you want to start with a G#2 on the small main and a G#2 and 2ea G#1's on the large main. If you currently are using Hoffman 75's two of them pretty much equals a Gorton #2.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Size of main vents required
Bob - On the smaller main I have a Gorton # 2, on the larger main I have 2-Hoffman # 75s and a Gorton # 1. So i guess the sizing I have is O.K.
Thanks for your input - I really appreciate your expertise. -cdm-0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements