uneven heating

New member - checked back 10 pages didnt see anything on my problem.



System: 1 pipe steam w/ cast radiators and 1 baseboard (in kitchen that never really works)



Situation: thermostat (on 1st floor) set @ 72 - 1st floor is 60º 2nd floor is 80º

Radiators on 1st floor are reading 130º 2nd floor ones reading 195º



Any ideas? Should also note that the temperature dropped to 9º which is abnormal for my area.

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    Baseboard never works

    This sounds like a main venting problem. Can you post pictures of them? Large main vents will allow the horizontal supplies to fill with steam first, and then slower radiator vents allow the steam to enter all radiators at the same time. Low pressure aids this, what is yours?

    Are the 2nd floor radiators on the same riser as the 3rd floor rads?

    Is the anticipator set properly on your thermostat?--NBC
  • Ducci356
    Ducci356 Member Posts: 2
    edited January 2014
    pics of system

    Pics of system



    Im not 100% sure but it looks like they r on the same riser