bryant 352 with LP conversion

ollies69
Member Posts: 4
I installed this furnace 8 years ago for a buddy, he called the other day and said it would not light. I found the roll out switch tripped and the intake pipe burnt. I replaced the primary and secondary heat exchangers as they where sooted up and plugged.
Now the furnace will go thru the normal start sequence I can only get 9 inches WC coming out of the gas valve and it will not light. I would think it should at least light with this pressure, the manual calls for 11 .
Now the furnace will go thru the normal start sequence I can only get 9 inches WC coming out of the gas valve and it will not light. I would think it should at least light with this pressure, the manual calls for 11 .
0
Comments
-
Gas valve orifice
Or maybe the regulator at the tank. Call the propane supplier on that.0 -
lp tank
I was thinking that also, but there is another furnace that runs from the same tank. I also checked the manifold orfices they are all clear.0 -
Can you
adjust the wc up at the valve? If not, then it must be the valve itself by process of elimination. Vents are all clear, right?.0 -
vents
I have cut both pipes open and checked them. I tried to adjust the wc. up more and the adjuster bottoms out at 9.
My next step was to replace the valve, I just never seen a valve fail like this before0 -
Solution
Ended up being a faulty gas valve0 -
Be sure
to clean off the flame sensor too, it probably has some carbon on it that will start to interfere with the signal.0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements