circulator size and hi-lo settings
HexHighway
Member Posts: 6
I have a client who owns a 3000 sf masonry home, and has oiled fired hydronic heat. The mains are 3" (formerly steam?) and the radiators at the end of the runs don't get super hot before the thermostat is satisfied (one zone).
It has one 007 Taco circulator and the aquastat is set at 160-180 with the diff at 20.
Is there any point in getting a larger circulator or upping the hi-lo or that wouldn't make an effective differrence?
It's just two of maybe 20 radiators that don't get very hot because they are the last on the run ...
So, what determines how you set the hi-lo and diff? And does the circulator size matter in a case like this? Thanks
It has one 007 Taco circulator and the aquastat is set at 160-180 with the diff at 20.
Is there any point in getting a larger circulator or upping the hi-lo or that wouldn't make an effective differrence?
It's just two of maybe 20 radiators that don't get very hot because they are the last on the run ...
So, what determines how you set the hi-lo and diff? And does the circulator size matter in a case like this? Thanks
0
Comments
-
If the supply and return are the same size
it was originally a gravity hot-water system, which did not use a pump.
Measure the square feet of radiation on that system, then use this chart to select the proper circ:
http://www.heatinghelp.com/article/343/Circulators/238/Sizing-Circulators-for-Hot-Water-Heating-SystemsAll Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks!
Very helpful. Great place to start. Thanks.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 65 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements