MM #42 vs a #67
Options
Tim Schram_2
Member Posts: 17
Just curious,
Is there any reason I couldn't use a #67 LWCO to replace a #42? The 67 has contacts to control feeding a water feeder too. Just curious. There is a boiler feed pump on the system for making up water.
Tim
Is there any reason I couldn't use a #67 LWCO to replace a #42? The 67 has contacts to control feeding a water feeder too. Just curious. There is a boiler feed pump on the system for making up water.
Tim
0
Comments
-
The #67 should not be used for a boiler-feed pump
Pumped-return requires the switches to activate every time the boiler needs water. The #67's switches aren't up to that job. They're fine for the occasional water feed on a gravity-return system, but that's it.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 119 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements