In a snow melt system with a mixture of 30% glycol cab you use a regular pump? Or it had to be a stainless steel one or bronze? Paul s
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    edited December 2013
    No…...

    problem, so long as you keep the corrosion inhibitor levels high, and 30% is the minimum recommended for corrosion inhibition protection on inhibited glycol, you will be fine.



    But you MUST check the fluid pH annually, and may have to induce additional inhibitors if the pH starts declining.



    If in doubt, and you can't guarantee fluid maintenance, then be safe and go non ferrous components.







    ME

    There was an error rendering this rich post.

  • Sam81
    Sam81 Member Posts: 37
    No

    Stainless and bronze are only needed for potable water or open system that can be damaged from oxygen
  • Paul S_3
    Paul S_3 Member Posts: 1,281
    inhibitors

    So the glycol itself has corrosion inhibition.....and what should the ph be?9? Thanks Paul s
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • hot_rod
    hot_rod Member Posts: 23,403
    PH of new

    inhibited glycol runs 10- 11.0 ph. It will drop as the inhibitors get used up. Below 8 PH it is time to consider flushing and starting with new product.



    If it is a good, tight, low temperature system, no O2 ingress, that fluid will last a long time. It pays to buy a good name brand, to be sure it has a good inhibitor package.



    If you have any aluminum components, you need a glycol inhibited to be aluminum friendly. Usually look for AL on the label.