circulator
Paul S_3
Member Posts: 1,281
In a snow melt system with a mixture of 30% glycol cab you use a regular pump? Or it had to be a stainless steel one or bronze? Paul s
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0
Comments
-
No…...
problem, so long as you keep the corrosion inhibitor levels high, and 30% is the minimum recommended for corrosion inhibition protection on inhibited glycol, you will be fine.
But you MUST check the fluid pH annually, and may have to induce additional inhibitors if the pH starts declining.
If in doubt, and you can't guarantee fluid maintenance, then be safe and go non ferrous components.
METhere was an error rendering this rich post.
0 -
No
Stainless and bronze are only needed for potable water or open system that can be damaged from oxygen0 -
inhibitors
So the glycol itself has corrosion inhibition.....and what should the ph be?9? Thanks Paul sASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
PH of new
inhibited glycol runs 10- 11.0 ph. It will drop as the inhibitors get used up. Below 8 PH it is time to consider flushing and starting with new product.
If it is a good, tight, low temperature system, no O2 ingress, that fluid will last a long time. It pays to buy a good name brand, to be sure it has a good inhibitor package.
If you have any aluminum components, you need a glycol inhibited to be aluminum friendly. Usually look for AL on the label.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements