Thermostatic Rad Valve Control
MikeyG
Member Posts: 10
<strong>Hi-</strong>
<strong>I am a homeowner and not a professional. I purchased the following products and installed them (after reading Dan's books) for one room where I have a second heating source to shut down the steam rad if the room reaches a certain temperature:</strong>
<strong>Thermostatic Rad Valve w/ Vac Breaker for one pipe steam -- Danfoss SKU:013G0140 </strong><span><span style="color:#000000">Remote Setpoint & Sensor - Wall Mount -- Danfoss SKU:013G8562 </span></span>
<strong>from Pex Supply</strong>
<strong>However, it does not seem to be working as the rad gets hot immediately regardless of the temp in the room (even if I adjust the thermostat of the remote sensor to the lowest setting.)</strong>
<strong>Can anyone suggest whatn the problem may be? Thanks in advance.</strong>
<strong>Mike G.</strong>
<strong>I am a homeowner and not a professional. I purchased the following products and installed them (after reading Dan's books) for one room where I have a second heating source to shut down the steam rad if the room reaches a certain temperature:</strong>
<strong>Thermostatic Rad Valve w/ Vac Breaker for one pipe steam -- Danfoss SKU:013G0140 </strong><span><span style="color:#000000">Remote Setpoint & Sensor - Wall Mount -- Danfoss SKU:013G8562 </span></span>
<strong>from Pex Supply</strong>
<strong>However, it does not seem to be working as the rad gets hot immediately regardless of the temp in the room (even if I adjust the thermostat of the remote sensor to the lowest setting.)</strong>
<strong>Can anyone suggest whatn the problem may be? Thanks in advance.</strong>
<strong>Mike G.</strong>
0
Comments
-
High and Low
EDIT
Removed as this is not the electric control I was referencing.0 -
non-electric
That looks to me as if the actuator is a non-electric (capillary) model, so it uses a tube and fluid pressure to control the actuator, not electricity. A multimeter won't help in that case.
In many cases if a capillary control is not working properly the capillary tube has been pinched or kinked at some point. With a kink, pinch, or hole in it the fluid can't transmit pressure from the dial to the actuator and it won't work. These capillaries aren't too delicate, but need to be handled with some care or they can be damaged (don't drop anything on them, put tight staples over them, or pull them tight around corners).0 -
Danfoss
the boiler/steam system must go to 0 psig on off cycle and have a numerous cycle rate for these 1 pipe valves to work correctly, if the system never draws air in the Danfoss valves often wont close. I posted the details in the past and believe I sent a document from Danfoss (1983) to the archivesThere was an error rendering this rich post.
0 -
r_stahmer@yahoo.com
type Danfoss in the site search look for July 29 2009 old document from Bill BurtonThere was an error rendering this rich post.
0 -
Cannot locate the details you posted in the past ...
Hi RJ.
I've tried to search for what you posted in the past and perhaps I just am not that good with searching this site but cannot find anything. Would it be possible to help direct me there? Thanks!
Mike0 -
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements