keeping things safe ....
jpf321
Member Posts: 1,568
So a friend of mine called me on Monday because he had no heat. He mentioned that his ignition control had melted (SF-8600). When I arrived, I think that it's lucky it melted. The following are the problems that he had ..
1) The bellows on his MM#67 LWCO float had accumulated some rust on the underside, therefore it would not freely drop when the water dropped .. it was being held up by only a few tiny specks of encrusted rust between the bellows sections. I could not believe that such a small amount of rust specks could keep the float from proper operation.
2) The *original 1989* 1/4" black street elbow that he had coming out of the top of his MM#67 to his brand new brass pigtail to brand new 404A Pressuretrol was plugged solid.
Obviously at this point he was sensing neither Pressure nor Low Water.
What had happened .. I think ...
On a cold day recently, the pop-safety blew and emptied all his water in fast action. The boiler kept going .. and melted his ignition.
We've since cleaned his #67 up nicely, we've replaced plugged black pressure El with a new brass one. We have replaced his pop-safety since he experienced it popped again on Monday night after we got him flame back monday afternoon. (after restoring flame on monday afternoon I alerted him to the problem with the #67 and we had scheduled it's overhaul for the next day, I did not notice plugged pressure elbow.)
I cannot stress enough that if you are reliant on a float-type LWCO (MM#67) you MUST test it WHILE THE BOILER is running to ensure proper operation.
The side of his boiler jacket was noticeably scorched. He was VERY LUCKY.
1) The bellows on his MM#67 LWCO float had accumulated some rust on the underside, therefore it would not freely drop when the water dropped .. it was being held up by only a few tiny specks of encrusted rust between the bellows sections. I could not believe that such a small amount of rust specks could keep the float from proper operation.
2) The *original 1989* 1/4" black street elbow that he had coming out of the top of his MM#67 to his brand new brass pigtail to brand new 404A Pressuretrol was plugged solid.
Obviously at this point he was sensing neither Pressure nor Low Water.
What had happened .. I think ...
On a cold day recently, the pop-safety blew and emptied all his water in fast action. The boiler kept going .. and melted his ignition.
We've since cleaned his #67 up nicely, we've replaced plugged black pressure El with a new brass one. We have replaced his pop-safety since he experienced it popped again on Monday night after we got him flame back monday afternoon. (after restoring flame on monday afternoon I alerted him to the problem with the #67 and we had scheduled it's overhaul for the next day, I did not notice plugged pressure elbow.)
I cannot stress enough that if you are reliant on a float-type LWCO (MM#67) you MUST test it WHILE THE BOILER is running to ensure proper operation.
The side of his boiler jacket was noticeably scorched. He was VERY LUCKY.
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements