EDR calculations

Many buildings in NYC use the steam risers to heat the bathrooms and kitchens.

When calculating the load for a boiler, how do you calculate the EDR for the risers. In my case they are 2 inch pipes, 30 feet in length.

Thank you.

Comments

  • SWEI
    SWEI Member Posts: 7,356
    Two inch pipe

    measures 7.46" in circumference, or 0.62177 square feet per lineal foot.  30 feet would have an EDR of 18.65 square feet.