Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
EDR calculations
baylis
Member Posts: 6
Many buildings in NYC use the steam risers to heat the bathrooms and kitchens.
When calculating the load for a boiler, how do you calculate the EDR for the risers. In my case they are 2 inch pipes, 30 feet in length.
Thank you.
When calculating the load for a boiler, how do you calculate the EDR for the risers. In my case they are 2 inch pipes, 30 feet in length.
Thank you.
0
Comments
-
Two inch pipe
measures 7.46" in circumference, or 0.62177 square feet per lineal foot. 30 feet would have an EDR of 18.65 square feet.0 -
Thanks
Thank You0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements