main return line traps

pugdad
pugdad Member Posts: 23
Hello looking for some advice on location and type of trap to install . have a two zone system blowing steam from condesate tank vent usally when only 1 zone is calling .there are 4 11/4 return line on each zone they drop out of crawl space aprox 4 ft and tee into single 11/4 line on each side to condesate tank . could a trap be installed on each of the two lines or would they need to be 8 traps one each of the returns prior to merging

Comments

  • Bad traps

    The problem must be further upstream, as no steam should come out of the returns from the radiators. Check all the radiator traps, and see if your problem is from higher up.--NBC
  • pugdad
    pugdad Member Posts: 23
    traps

    There are no radiator traps
  • Steamhead
    Steamhead Member Posts: 17,317
    Take a picture

    of one or more of your radiators and post here- let's see what you have.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • pugdad
    pugdad Member Posts: 23
    traps

    sorry no pic of radiators ,single pipe former contactor installed condensate tank with no traps
  • Steamhead
    Steamhead Member Posts: 17,317
    I'd be willing to bet

    you don 't need that condensate tank at all. Gravity return worked for the Dead Men......
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • JStar
    JStar Member Posts: 2,752
    edited November 2013
    Traps

    How high is the water level in that picture?