how to wire a vaporstat in series with presure control
Nation
Member Posts: 2
I have been reading many threads that recommend wiring the pressure control as a backup for the vaporstat. How do I series these properly I can only get one or the other to work. I currently just have the vaporstat wired up on the R and B terminals. Wich terminals would I wire the pressure control to. Both of these are Honeywell controls by the way.
0
Comments
-
Wiring
Let's assume that the controls are exactly the way they came from the factory. After you install the Vaporstat, run a wire from it to the existing Pressuretrol. Take one wire off of the P-trol terminal. Wire nut that wire to one wire from the V-stat. The other wire from the V-stat goes to the P-trol terminal.
Think about series wiring as completing a circle.0 -
thank you
Yes this makes sense thank you for your help.0