How Much Can You Downfire an IN5 ?
Rod
Posts: 2,067
Hi-
Need some advice on an oversized boiler situation.
The total EDR of the system is 230.10 Sq.Ft
The boiler that should have been installed was an IN4 @ 271 sq. ft of steam (IBR Net)
The boiler that was installed was an IN5 @ 358 sq. ft of steam (IBR Net)
The result is that the present boiler is 128 sq. ft. oversized.
Now the question is: How much can you down fire an IN5 ?
Thoughts?
Thanks for your help!
- Rod
Need some advice on an oversized boiler situation.
The total EDR of the system is 230.10 Sq.Ft
The boiler that should have been installed was an IN4 @ 271 sq. ft of steam (IBR Net)
The boiler that was installed was an IN5 @ 358 sq. ft of steam (IBR Net)
The result is that the present boiler is 128 sq. ft. oversized.
Now the question is: How much can you down fire an IN5 ?
Thoughts?
Thanks for your help!
- Rod
0
Comments
-
Down-firing Burnham atmospheric
This may be a question for the Burnham tech support. Possibly, the nozzles could be changed in the burner to reduce the fire evenly across the bottom.
Situations like this make it even more important to have the venting and balance as good as possible, with massive main venting, and slow rad vents.--NBC0 -
Oversized Boiler
Hi Nick- Thanks for the reply! I'm going to suggest increasing the main venting.
- Rod0 -
Venting/two stage gas
You can increase the radiator vent as well or add a two stage gas valve controlled by a vaporstat, and run on low to match EDR, here is a picture of one of Gerry Gill's installation0 -
Two stage retrofit on natural draft boiler
very interesting. Got a link, or more information?
thanks~0 -
Link
I'm a H.O. and I did some research for my tenants oversized boiler but boiler broke a leak early this year and had to be change, but check these couple of links
http://www.heatinghelp.com/forum-thread/127199/2-stage-gas-burner
http://www.heatinghelp.com/forum-thread/134762/down-firing-an-atmospheric-burner0 -
I did it
I had an oversized Burnham IN-6 in my house, which is basically the same as an IN-5, except with one more section. I contacted Burnham and they told me that it could be downfired no more than 10%.
For natural gas at normal elevations, these boilers come with #45 (pink) orifices, part number 822711. #47 (white) orifices, part number 822710, will downfire the boiler about 10% compared to the #45. I made that change on my boiler and it went a long way to quieting the nasty hissing radiator vent issue I was experiencing. (Yes, I had already vented the snot out of the main.) I clocked the gas meter before and after to confirm the reduction in gas use. I also did before and after flue gas analysis which confirmed that the boiler was still operating properly.
I ran it that way for only one heating season, and I didn't notice any fuel savings . . . just a quieter system with less short cycling. I got a great deal on a smaller (IN-5) boiler the next summer and replaced the IN-6 . . . resulting in another 10% reduction in steam output. This set-up seems to be the sweet spot for me . . . a nice quiet system that fills all the radiators evenly and almost never cycles off the pressuretrol.
YMMV0 -
Thanks!
Still have some questions on the piping, but this looks quite promising.0 -
How Much Can You Downfire an IN5 ?
Thanks everyone for your input!
- Rod0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements