How Does this Install Look?
saikosis
Member Posts: 75
My father just had his hot water boiler replaced because of a crack in the block. He had the work done by one of the contractors that I considered for putting in a new steam boiler for me. I was curious what you guys thought of his work. Note that this guy is NOT listed here.
The first two are the old boiler and piping.
The first two are the old boiler and piping.
0
Comments
-
The Install looks nice.
Apparently the guy has an eye for neatness, which is a good thing!
There are some things we do differently with the piping. It is always best to put the circulators on the supply side, pumping away from the expansion tank. Primary-Secondary piping is also the preferred method. In a header and branch system like the picture shows, the circulator controls must be integrated into the triple aquastat and not allowed to come on until the boiler reaches approximately 140°.0 -
Nice clean Install
Good luck with your new system Looks great stay warm my friend Dan0 -
Primary Secondary
I don't know the flow rates of the zones but I would not feel comfortable not having primary secondary piping on that system. The installer did obviously take pride in his or her workmanship.
JMHO,
Rob0 -
Comments
1. Not "pumping away", which adds air to system
2. 1 (Smart) pump and 5 zone valves would have used 70% less power
3. No pipe insulation
4. No outdoor rest control
Otherwise, the system was assembled with some craftsmanship, but there's more to it than shiny copper and a row of pumps.0 -
Feedback
Thanks for the feedback. The guy was very neat and professional. He actually had seven guys on site for the install. My father said there were so many people and so much material flying around that he thought the install would be a disaster, but he was pleasantly surprised when the dust settled.
I know a little about steam, but nothing about hot water systems, so I'm not sure what pumping away means or what primary-secondary piping is. I'll try to read up on this stuff. In the mean time, can I turn the question around and ask what problems might pop up that my dad should watch out for?
I appreciate the help.0 -
fixes
Do you think the owner has the right to ask the installer to do any of the changes recommended here?0 -
Not Really
Except maybe the primary secondary piping if the install requires it, and there ends up being problems.
Zoning with circs verses zone valves involves more energy consumption.
Pumping away from the expansion tank facilitates better air removal in the system.
Pipe insulation is going to keep the btus in the piping to get where they need to be.
Outdoor reset is another energy conservation option.
Its tough for a homeowner to know what they should be getting for the most energy efficient system possible. And know proper piping practices, zoning options etc.
Bottom line its the difference between the highest price install, and the lowest price.........but not always.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements