Earlier this year we were called for a no-heat at this mission, which shelters homeless people. What we found was a leaking Weil-McLain LGB-8, lots of asbestos, a condensate pump feeding into a boiler-feed pump and a bunch of rotted-out piping around the pumps. And there was no way to keep steam out of the tanks, so the boiler room had been a sauna for years.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
0
Comments
-
We installed a W-M 7-80 and Carlin 301Gas
and a whole bunch of Gorton #2 main vents, after the asbestos crew had done their thing. The new boiler has two 4" steam risers instead of just one on the old one, and a drop header, so we're making much dryer steam. A Vaporstat keeps the pressure low, and we went back to good old-fashioned gravity return.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Nice Work
I love seeing pictures of your work. I take away a little nugget of information each time. I do have a question though, this isn't criticism, it's a real question. Why don't you insulate the risers from the boiler? I see most pros don't and I haven't read anything about why not to do it yet. Is there a specific reason?0 -
Yup
someone else was doing that, and they ran out of 4-inch insulation.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Looks Familiar!
Steamhead, another beautiful install! I am happy to see how much it resembles my 680 install last year. It was a fantastic install by "boiler wrestler", who reads this forum and occasionally comments.
Just for comparison,
https://www.facebook.com/media/set/?set=a.502972719744401.109158.142994895742187&type=1Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
On The W-M 80 series Boilers...
The instructions call for the pressure control tree to be mounted from a tapping on the front of the boiler.
We think that is radically unsound!
It is too close to the waterline and the 1/2" pipe and fittings supplied are more likely to get filled with rust and sludge rendering the controls inoperative.
As an aside, Washington D.C. codes require all steam piping 1" and under to be sch. 40 brass! That may be going a bit far, and it still does not answer the issue of sludge.
We therefore mount the pressure controls off of a top tapping and above the active waterline.All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
Good Point
You make a good point. Mine was installed according to WM guidelines. The installer left a capped nipple at the side of the tree so that I can flush it out, as it did this fall prior to start up. I am thinking about installing a ball valve to make it easier. I have heard that some inspectors require a valve so that the control tree can be blown down.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Drop Header Q
I have seen some instances on this site where the drop headers dimensions were increased relative to the risers to help facilitate dry steam. Do you think that is overkill, a good idea, or does it depend on the circumstances?
A good story for a good cause BTW.0 -
Nice job Frank!
looks like a tight place to work! Your not a spring chicken anymore either, how are you getting the boiler sections down into the dungeons? got any young bucks helping?gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
The delivery crew
from Ferguson's has a stair climber so they took the sections in. Earlier we had disconnected the old boiler for a group of volunteers to remove. They scrapped the old boiler and I believe gave the proceeds to the Mission.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Depends
this one goes into what was the header for an old boiler that was there before the LGB. It's 5-inch, so it slows the velocity even more. We call this the "doubleheader" hookup.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements