B & G Circulator Pump Exercise?
MikeJL
Member Posts: 9
So heating season upon us again and fired up my little cast iron Utica with 6 B & G NRF-9F/LW circulators pumping thru my radiant floor system. Have a locked up pump again in one zone. Swapped it out with spare and up and running again but have a question about keeping these little pumps from locking up in the off season. B & G makes a controller that tickles the pumps for 10 seconds every 72 hours if there is no call for heat. I have an ARGO 866 control board. Is there any "module" I can add to the ARGO to get it to exercise these pumps in the off season? Any other automatic way to handle this, I will never remember to do it manually. System is about 13 years old.
I have reused the locked up pumps by pulling the cartridge and manually turning the impeller back and forth until it turns freely again. If you reinstall it right away it runs fine with the system water lubricating/cooling the pump. If it sits it will tend to lock up again. Any recommended way to mothball these used pumps? Closed system with no problems with water quality.
I have reused the locked up pumps by pulling the cartridge and manually turning the impeller back and forth until it turns freely again. If you reinstall it right away it runs fine with the system water lubricating/cooling the pump. If it sits it will tend to lock up again. Any recommended way to mothball these used pumps? Closed system with no problems with water quality.
0
Comments
-
most of the pump control boxes
have this feature built in.
You could buy a simple lamp timer and adjust the pins to run once a day for a few minutes, or an electronic timer that you could build any schedule. Power this timer with the same circuit that powers the relay box.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Know I can buy a new 6 zone control box
but was looking for workaround......your idea of wiring a timer up to run the pumps periodically in the off season would do the trick. Also have tech support question/request on this issue into ECR ARGO but has been a few days.....probably not at the top of their list for help so appreciate your comments/help hot rod.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements