Fewer Circulators with 3-way diverter valve

optimist55116
Member Posts: 12
I am adding an indirect water heater to my hydronic heating system and updating the design a little. In the process, I am trying to reduce the number of circulators. In the typical drawings of a system with a non-condensing boiler, a buffer tank, and an indirect, each has its own circulator pump. Couldn't I eliminate two of these pumps with a 3-way mixing/diverter valve (motorized). Assume that the indirect gets the full attention of the boiler when calling. The following is a sketch of what I am thinking (with many non-relevant components not drawn here):
0
Comments
-
Sure
As long as has adequate Cv for the load. What size boiler?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks and ...
Cv is around 20 and boiler takes in 130K (so about 100K) out. I0 -
The few I have done
We're 80K boilers. I put the zone valve on the return piping. Cooler temperature and less delta P. I used a common paddle style, spring return ZV with a 7.5 Cv 1" sizeBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 771 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
- 17 Recall Announcements