Fewer Circulators with 3-way diverter valve

optimist55116
Member Posts: 12
I am adding an indirect water heater to my hydronic heating system and updating the design a little. In the process, I am trying to reduce the number of circulators. In the typical drawings of a system with a non-condensing boiler, a buffer tank, and an indirect, each has its own circulator pump. Couldn't I eliminate two of these pumps with a 3-way mixing/diverter valve (motorized). Assume that the indirect gets the full attention of the boiler when calling. The following is a sketch of what I am thinking (with many non-relevant components not drawn here):
0
Comments
-
Sure
As long as has adequate Cv for the load. What size boiler?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks and ...
Cv is around 20 and boiler takes in 130K (so about 100K) out. I0 -
The few I have done
We're 80K boilers. I put the zone valve on the return piping. Cooler temperature and less delta P. I used a common paddle style, spring return ZV with a 7.5 Cv 1" sizeBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements